AFCI branch circuit tripping when 220 range circuit is on
devildog6687
New member
Centre Hall Pa
We have an AFCI branch circuit that trips after range is on for five minutes. This happens consistently and has start two years after the arc faults were installed. The branch circuit is good and does not trip but will when range is on with regularity. Any ideas we are stumped.
Nothing surprises me anymore with afci or gfci circuits. I would try a different afci breaker and see what happens. I have no idea why that would happen.
Weird coincidence guess:
1. Range circuit has an at least slightly crossed neutral with the circuit under test. Or at least a neutral to ground bridge.
2. A heating element of the range develops a high impedance short from resistor winding to grounded metal shell of heating element only after it has warmed up for 5 minutes. Or other temperature sensitive leakage.
OR
Constant very low level ground imbalance in the affected circuit when the range is on. A current in the range near 20ma can take a considerable time to trip the GF detector component in the AFCI.
OR
I don't understand how (2) would cause an afci on a different circuit to trip unless there was some connection between them
We all have seen gfci's trip when a different circuit trips. It's voodoo
I was assuming some sort of cross connection for the second case too, I just did not state it explicitly.
A judicious application of chicken blood will often cure it.