AFCI branch circuit

Status
Not open for further replies.

Ken 6789

Senior Member
Does light fixtures in bedroom dwellings have to be on AFCI protected circuits? Also, someone told me that if you wired your home in emt, flex, or mc then you are not required to put bedrooms on AFCI protected circuits. I was always under the impression that not only does AFCI's protects against arcs in the line, including cords you plug in receptacles. If that's the case then you would still need to put the bedroom circuit on AFCI's even if it is in emt, flex, or mc. Thank you in advance.
 
Last edited:

stickboy1375

Senior Member
Location
Litchfield, CT
1099599192_2.jpg
 

480sparky

Senior Member
Location
Iowegia
The wiring method is irrelevant in terms of it being required. 210.12

The only difference with regards to the wiring method used is the placement of the arc-fault protection. 210.12(B) Exceptions.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
cadpoint said:
Yeah they don't need a light on the fan cause the room with glow with the switched service :rolleyes:
Jude, that my friend might be sentence of the week. You just won a "Toys For Tots". How would you like that shipped?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
stickboy1375 said:
I thought the bold red letters at the bottom of the picture were pretty clear?

You keep changing the picture tho. That's your 3rd avatar in as many days. Are you bored????:grin:
 

cadpoint

Senior Member
Location
Durham, NC
Toys for tots

Toys for tots

I think You meant , My Edit IS

chris kennedy said:
Chris, my friend might the sentence of the week be. You just GIVE To "Toys For Tots". How does one go about supporting this ship?

:rolleyes:
On Post, YES AFCI is standing order of NFPA-70 08', but depending on the Local Authority Regulations, and there actions on this matter.
 

celtic

Senior Member
Location
NJ
Ken 6789 said:
Does light fixtures in bedroom dwellings have to be on AFCI protected circuits?


According to the NEC - yes, regardless of wiring method.
According to the ameneded version NJ is using - it's "optional" for AFCI protection, regardless of wiring method.


Not knowing where you are located, the answer would be - YES
 

hulk

Member
Location
chicago
afci

afci

Do we have to mark the neutral with different color tape for arc faults or is it cheaper and more common to buy white wire with tracers?
 

celtic

Senior Member
Location
NJ
hulk said:
Do we have to mark the neutral with different color tape for arc faults or is it cheaper and more common to buy white wire with tracers?

Why do anything with them except terminate them?
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
hulk said:
Do we have to mark the neutral with different color tape for arc faults or is it cheaper and more common to buy white wire with tracers?
Welcome to the Forum, Hulk.:smile:

Your location gives the hint that you run a lot of pipe in residential settings. Am I right?

There is nothing in the NEC that says a neutral that is protected by an AFCI has any special additional identification required beyond that of all other neutrals.

The practical point of the matter. . . .the AFCI will trip if the protected neutral is cross neutralled to another circuit, or if the neutral connects to the equipment grounding conductor. If using a white or grey with a tracer helps an installer to get the installation right the first time, when s/he has a history of errors otherwise, well, why not?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
the new code says we can use them instead of afci breakers as long as we run emt, rigid or steel ac and use a metal box..but whos going to do this?
About 60% of the population of the State of Illinois where the local codes require the use of EMT for dwelling units, that is assuming that an AFCI receptacle would be more cost effective than an AFCI breaker.
Don
 