AFCI breaker requirements

Status
Not open for further replies.

jetlag

Senior Member
I wanted to be sure what type of breakers are required now for residential construction . I know every 120 v outlet has to have AFCI protection now . I have already installed GFCI receptacles in the proper locations . I know they have breakers now with both AFCI and GFCI protection . Is it ok to leave the GFCI receptacles in place and use a regular AFCI breaker for those circuits ? I know also that the AFCI breakers now are CAFIC .So that is what I would use . I understand the C is for continuous in the same lead like between two conductors in a wire nut . What am I missing ? I thought AFCI breakers always did that before they added the C . If someone can advise me what breakers are required now , I will be grateful . thanks
 
I wanted to be sure what type of breakers are required now for residential construction . I know every 120 v outlet has to have AFCI protection now .
Not "every" but most
I have already installed GFCI receptacles in the proper locations . I know they have breakers now with both AFCI and GFCI protection . Is it ok to leave the GFCI receptacles in place and use a regular AFCI breaker for those circuits ?
Yes
I know also that the AFCI breakers now are CAFIC .So that is what I would use . I understand the C is for continuous in the same lead like between two conductors in a wire nut . What am I missing ? I thought AFCI breakers always did that before they added the C . If someone can advise me what breakers are required now , I will be grateful . thanks
The "original" AFCI protected against parallel arcing, the "c" or combination are for parallel & series, a second generation
 
"DF" or dual function AFCI breakers will have both GFCI and AFCI functions. Probably cheaper to use them instead of an AFCI and GFCI receptacles.

I really wouldn't worry about the combination "C" devices if I had to choose. Use the cheapest that satisfies code.

-Hal
 
. If someone can advise me what breakers are required now , I will be grateful . thanks
You must use "combination" AFCI (tha'ts about then only type you will find unless someone has oldddd stock) OR
dual function AFCI/GFCI
Exact requirements by circuit will depend on which Code cycle and local amendments.
 