Re: AFCI compatability w/shared neutral feeds?
At the IAEI convention, AFCI's were a hot topic as we can all guess why. Some important information was brought forth. I will to the best of my ability in as short a format as possible explain what I heard.
1. AFCI do not moniter hot to neutral, they have micro chips that detect the 'signature' sign wave of particular 'Arc faults'. This is the significant difference between the AFCI and the GFCI.
2. Most AFCI are set to trip (depending on the manufacturer) at 50 to 75 amps from an 'arc fault'. Lower values were causing nuisance tripping.
3. Most if not all manufacturers are producing their AFCI's with GFCI protection set at around 40 milliamps. These are not listed as combo units as some have suggested.
4. Square D has now (as of Sept 2, 03)come out with a 'combination' AFCI Breaker. Combination in the sense that it will protect the circuit from an arc fault, and a utilization equipment plugged into the receptacle. They say this is a first in the industry. They will not be readily available for a few monthes. Because of the new technology they are able to have the AFCI detect faults as low as 5 AMPS. Much lower than even their previous Arc fault breaker.
5. A large percentage of the arc fault breakers tripping have been found to be wiring mistakes. The manufacturers want to be able to further develop the product, and will send a technician out to your site if you are experiencing problems. In this process they have learned that 90% of the problems in the field are neutral to ground connections in the circuit that are tripping the device.
Because AFCI's are not going to disappear, I suggest two things. Get the manufacturers to come to a local meeting to educate the members as to the functions and trouble shooting process for the devices. And contact them for any problem or info, as any and all will help in the future development of the product.
Because the GFCI protection of an AFCI breaker is set at 40 milliamps, some breakers are not tripping until a load is introduced on the circuit. A 4-6 amp class 'A' GFCI trips almost instantaneously, because it does not take too much leakage current in the circuit to trip it. On the otherhand a 40 milliamp device will not detect the low level leakage and therefore a load will need to be introduced. That is why some will say the breaker does not trip until they turn the fan, light or whatever on. In this case 'most' times it is a neutral-ground connection somewhere in the circuit.
There is a race on with the different manufacturers to put the best product out. Because of this they are working with us on this. I made a suggestion for them, produce an AFCI that will indicate when it has tripped, if it tripped on GFCI or AFCI. Wouldn't that solve some issues?
Contact the manufacturers with your suggestions!
Pierre