http://ecmweb.com/mag/electric_illustrated_changes_nec_7/Arc-fault detection does not replace other aspects of circuit protection. Short circuits from essentially bolted conditions must be still cleared instantaneously. Long term overloads must still be cleared on an inverse-time basis, with greater overloads clearing more rapidly. Although the arc-fault detection mechanism will be inside a typical molded-case circuit breaker, its sensing mechanism is strictly in addition to the conventional components. AFCI protection doesn't substitute for GFCI or GFPE protection, either. These devices are residual current devices: They measure the total current in a circuit, going to the load and returning from the load. If the vectorial summation of all currents does not equal zero, these devices detect the amount of that residual current and trip above a predetermined point. AFCI protection does not duplicate any of these functions, although a manufacturer may well marry some of them within the same device. An AFCI detects and clears arcing faults whether line-to-line, or line-to-neutral, or line-to ground. In spite of outward similarities in appearance, don't confuse an AFCI circuit breaker and a GFCI circuit breaker.
Basically, AF and GF look for different characteristics in a circuit that initiate the "trip".
:-?Your reference is 10 years old. There may have been improvements.
My question is: if the manufacturer of the device states it will clear a 30 ma ground fault, is there any reason it can not be used for GFPE protection of electric heat tracing? Obviously, if the device does not have the capability, it can't be used.
How many people think the Combination AFCI breakers are GFCI and AFCI, together in one breaker ?
I doubt if you find an AFCI that is listed for use as a GFPE device, but all AFCIs have a 30 to 50 mA ground fault trip unit. In most cases the ground fault device, and not the fancy arc signature recognition device causes the AFCI breaker to open the circuit. It is almost impossible to have a 5 parallel arcing fault without also having a 30 mA ground fault. In most cases the AFCI does not even detect a poor or glowing connection, (some times called a series arcing fault) until the heat from the fault has caused enough damage to turn the fault into a ground fault or parallel arcing fault.I'll go with that George...if documentation showing the AFCI is suitable as GFPE can be produced.