B Broncot77 New User Location Banner09! Occupation Electrician Mar 29, 2024 #1 I did a panel upgrade with afci gfci QO breakers when I turn power back on multiple trip immediately.
I did a panel upgrade with afci gfci QO breakers when I turn power back on multiple trip immediately.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 29, 2024 #2 Do you have MWBCs? Or you have found a neutral to ground connection in a j box
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Mar 29, 2024 #3 Neutrals and hots to the same breaker?
tortuga Code Historian Location Oregon Occupation Electrical Design Mar 29, 2024 #4 What is the breaker LED telling you? ground fault or arc fault?