When a AFCI/GFCI is installed in a subpanel, where does it get it's ground reference? Even if it's not a GFCI, all the combination AFCI's have gfci circuits. Thanks
L1 Bus ------- Regular Breaker ----------
|
Load
|
N Bus -----------------------------------
L1 Bus ------- GFCI ---------------------
Breaker |
With Neutral Load
Routed |
N Bus ---------Through It----------------
The "ground reference" really doesn't have anything to do with how a ground fault is detected. The current flowing in the hot conductor is compared to the current flowing in the return conductor. Under normal conditions the two currents are equal, but flowing in opposite directions. When the hot and return currents differ, by as little as 5 milliamps, the circuit interrupter operates.When a AFCI/GFCI is installed in a subpanel, where does it get it's ground reference? Even if it's not a GFCI, all the combination AFCI's have gfci circuits. Thanks