Afci/Gfci Multi-wire circuits

Status
Not open for further replies.

linn

Member
When you install a multi-wire circuit,using either AFCI or GFCI receptacles,is it allowed to share the neutral?
I haven't been able to find a code reffering to this type of installation.
 

bphgravity

Senior Member
Location
Florida
Re: Afci/Gfci Multi-wire circuits

I don't beleive there are any afci receptacles on the market yet, but they do exist. GFCI receptacles can be served from a multiwire branch circuit, however, a multiwire branch circuit can't be served from a single-pole gfci or afci circuit breaker.
 

peter d

Senior Member
Location
New England
Re: Afci/Gfci Multi-wire circuits

If you are stuck in a situation where you need to GFCI or AFCI protect a multiwire circuit, you have the option to use very expensive 2-pole GFCI and AFCI breakers.
 

aelectricalman

Senior Member
Location
KY
Re: Afci/Gfci Multi-wire circuits

I feel fairly certain that they will never allow AFCI's to become a receptacle in a dwelling unit. The point of the AFCI is to be installed at the origin of the branch circuit or feeder, such as at a panelboard, where it can function to de-energize the entire branch circuit when an unwanted arc is detected. If the AFCI becomes available to use as a plug, then what happens to the feed in coming from the panel to the AFCI receptacle? It is not AFCI protected!
 

aelectricalman

Senior Member
Location
KY
Re: Afci/Gfci Multi-wire circuits

Im not saying they don't exist or can't be used in certain situations. Im just saying I doubt the NEC would ever allow it in a new dwelling unit as a primary source of AF Protection.

[ January 24, 2005, 08:43 PM: Message edited by: aelectricalman ]
 

charlie

Senior Member
Location
Indianapolis
Re: Afci/Gfci Multi-wire circuits

An AFCI will be permitted by the 2005 NEC. Take a look, you will be permitted to use up to 6 ft of a metallic wiring method to a receptacle without AFCI protection. This opens up the ability for the AFCI receptacle to be used. By the way, I think it has already been built but it is not on the market. :D
 

aelectricalman

Senior Member
Location
KY
Re: Afci/Gfci Multi-wire circuits

I figured if it did become permisable there would be some restrictions. Like you stated, 6'. I guess they allowed this provision just for the reason of permitting receptacles huh. Cool.
 

linn

Member
Re: Afci/Gfci Multi-wire circuits

I contacted the people at Leviton and Hubble,neither one is making an AFCI receptacle at this time.
I also understand that there is a certain amount of controversay pertaining to the effectivness of the AFCI breakers themselves.
I believe they may have put them out there as a requirement before they did enough R&D.
 