AFCI/GFCI

Status
Not open for further replies.

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
Kitchen remodel questions

Existing SABC not touched or extended they are countertop receptacles including the refrigerator. I assume I do not need any AFCI but must GFCI receptacles accessable to the counter top but not the refrigerator. There is no sink issue there


new recpt in upper wall cab for microwave. Assume AFCI but no GFCI it's not a counter top recpt but is within 6' of sink


Dishwasher new circuit cord and plug connection under sink AFCI & GFCI

Garbage disposal new circuit cord and plug AFCI no GFCI recpt is under sink

2014 Code
 
Any recep you replace must meet current requirements, this started in 2014 code. Countertop recps must be afci, gfci and tr
 