jmo103
Member
- Location
- Boston, MA, USA
Article 210.12(A)(6) tells me that if I run an MC to the first outlet I can use an AFCI device to protect "the remaining portion of the branch circuit." My question is, if that outlet is the only outlet on the circuit, does it need to be an AFCI device? There is no remaining portion to protect.
The situation is in a finished basement with the panel next to the washer and (gas) dryer. There is a tankless water heater there too. I was hoping to use 3 15' runs of 12/2 mc (which I have laying around), and save $120 on 3 AFCI breakers. Would that be a compliant install? I am having trouble getting in touch with the inspector to ask the question because he has about 15 minutes of office hours daily.
The situation is in a finished basement with the panel next to the washer and (gas) dryer. There is a tankless water heater there too. I was hoping to use 3 15' runs of 12/2 mc (which I have laying around), and save $120 on 3 AFCI breakers. Would that be a compliant install? I am having trouble getting in touch with the inspector to ask the question because he has about 15 minutes of office hours daily.