Proposals Report of CMP-2 o 2-134a - ( 210.12(B) ): Accept o (B) has been revised stating " a listed AFCI, combination type installed to provide protection of the branch circuit". With an Exception, for location being permitted at other than the origination of the branch circuit under (1) AFCI installed within 1.8 m (6 ft) of the BC overcurrent device and (2) circuit conductors between the overcurrent device and AFCI are in metal raceway or a cable with a metallic sheath.
Is this proposal implying that AFCI type receptacles will be allowed for the 2005 code cycle?
Considering that AFCI's are required for Dwelling Units only, how many installations in dwelling actually use a metallic conduit or metallic sheathed cable for bedroom branch-circuits?
What is the 6' distance mean? Does it mean that the AFCI receptacle would have to be within 6' of the loadcenter? If this is the case, how many loadcenters are installed within 6' of the bedrooms?
I dont see how this new proposed exception can be utilized or even usefull, or am I missing something in the intent?