Guys what’s your opinion on AFCI protection in (Dwelling units) Bathroom.
The NEC does not address it.
The NEC does not address it.
An arc fault condition may occur in the bathroom itself or in the attic, in my opinion the bathroom requieres AFCI protection but the code does not address it.. would the AHJ have the last word on it..?
For about every other situation no. Used to have similar wording until 2017 when they did add the word kitchen to the list.210.12(C) is a new Section in the 2014 NECthat requires AFCI protection for the branch circuits supplying 125V, 15A or 20A outlets in dormitory bedrooms, living rooms, hallways, closets and similar rooms.
Similar...Rooms?
Is a Bath Room similar to a Kitchen, Laundry Room,............?
210.12(C) is a new Section in the 2014 NECthat requires AFCI protection for the branch circuits supplying 125V, 15A or 20A outlets in dormitory bedrooms, living rooms, hallways, closets and similar rooms.
Similar...Rooms?
Is a Bath Room similar to a Kitchen, Laundry Room,............?
Bathroom is also defined in NEC. most other rooms on the list are not NEC defined.Look at the definition of a kitchen---there is no way in the world that one can compare a kitchen to a bathroom.
Hi Don,For those that have the first edition of the 2020 handbook, you will be mislead into believing that AFCI is required for all 120 volt, 15 and 20 amp branch circuits. That is not correct and is based on the vote on the floor of the NFPA meeting that would have required that protection. When there is a floor vote on a rule change that is accepted, the rule returns to the code making panel and must receive a 2/3s majority to become part of the code. The vote at CPM2 was 7 to 7, and per the NFPA rules, the language in the 2020 code reverts back to the most reason language that had consensus...that is the language in the 2017 code. There is no change in the areas that require AFCI protection in the 2020 code.
For "dwelling units" I don't think there was any changes as far as what rooms require AFCI since 2014 as a general rule. That is when they added kitchens and laundry areas and included "devices" along with "outlets".Hi Don,
Am I to understand that AFCI requirements gave not changed since the NEC 2017 code book was published? Do you know where I can access the information you just posted above?
Or is it in the second addition of the NEC 2020 Code book?
Thanks
The actual code book is correct. It is only the handbook that is wrong.Hi Don,
Am I to understand that AFCI requirements gave not changed since the NEC 2017 code book was published? Do you know where I can access the information you just posted above?
Or is it in the second addition of the NEC 2020 Code book?
Thanks