AFCI protection question

Status
Not open for further replies.

mdb94

Member
Location
Arizona
In reference to the 2008 NEC, do non-livable areas such as garages, patio's and floodlights need to have AFCI protection? If not, where can I find this in the NEC? Thank you, Chris
 
In reference to the 2008 NEC, do non-livable areas such as garages, patio's and floodlights need to have AFCI protection? If not, where can I find this in the NEC? Thank you, Chris
Look at 2008 NEC 210.12. It lists where AFCI protection is required, and is silent about where it is not required. Garages, patios and outside floodlights, as nothing is said about them, are not required to have AFCI per the 2008 NEC.
 