afci recptacles

Status
Not open for further replies.

reeveselectric

New member
I was very interested in the dialogue regarding afci receptacles. One point that no one seemed to mention as a plus point on AFCI recptacles over AFCI breakers in protection of branch circuits and cords in older houses is that in an older house that has been wired with old 3 wire BX ( which is a common in the Washington DC area) AFCI protection is not possible by circuit breakers but would be if there was a AFCI feed through receptacle that could protect selected portions of the circuit. Has anyone else encountered this situation?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A 2 pole AFCI circuit breaker will protect both circuits of a 3 wire MWBC. The question is are they available especially for older panelboards.
 
Status
Not open for further replies.
Top