afci required ?

Status
Not open for further replies.

wireman1

Senior Member
we are still using the 2008 code in pa. if you run a new circuit from the panel to the bed rooms for lighting or recpes . the wires will be fished as the walls would not be opened up as you do when remolding must you use a afci .receptacle or circuit breaker to protect this circuit
 

480sparky

Senior Member
Location
Iowegia
Protection must be provided. There's no exception for 'added' circuits or 'fished' circuits. New circuits require AFCI.
 

david

Senior Member
Location
Pennsylvania
we are still using the 2008 code in pa. if you run a new circuit from the panel to the bed rooms for lighting or recpes . the wires will be fished as the walls would not be opened up as you do when remolding must you use a afci .receptacle or circuit breaker to protect this circuit

remolding must you use a afci .receptacle or circuit breaker to protect this circuit

I would hope you would do this alteration in compliance with the NEC. If your asking is it required than, NO.

PA. uniform Construction Code
§ 403.1. Scope.
(1) The Uniform Construction Code applies to the construction, alteration, repair, movement, equipment, removal, demolition, location, maintenance, occupancy or change of occupancy of every building or structure which occurs on or after April 9, 2004, and all existing structures that are not legally occupied.
(b) Exclusions and exemptions. The Uniform Construction Code does not apply to:
(8) Alterations to residential buildings which do not make structural changes or changes to means of egress, except as required by ordinances in effect under sections 303(b)(1) or 503 of the act (35 P. S. § § 7210.303(b)(1) and 7210.503). Under this subsection, a structural change does not include a minor framing change needed to replace existing windows or doors.
(9) Repairs to residential buildings, except as required by ordinances in effect under sections 303(b)(1) and 503 of the act.
§ 7210.103. Definitions
“Residential building.” Detached one-family and two-family dwellings and multiple single-family dwellings which are not more than three stories in height with a separate means of egress which includes accessory structures.
 
Last edited:

JFletcher

Senior Member
Location
Williamsburg, VA
210.12(B) of the 2008 NEC would require AFCI protection for bedroom outlets (lights and receptacles).

PA may have amendments, exceptions, or use the IRC for one and two family dwellings, like VA does (we are on the 2011 NEC and 2012 IRC). Even here AFCI are required for new bedroom circuits.

eta: if you are using the 2008 code as-is, no amendments, you must use an AFCI breaker if fishing NM as that wiring method does not meet exception #1 for using an AFCI receptacle.
 