I did a search before posting this and noticed three other recent threads on the topic of AFCIs. I read some of the content and will go back and read the rest:
The call came in this morning, husband and wife wanted someone out there right away to check 3 or 4 breakers that repeatedly kept tripping. On the phone he said, "It's weird."
I pulled up to a newer house, 2 or 3 years old, of the style popular nowadays here in the south-middle-west, white with natural wood trim. The house is newer, but the neighborhood is older, and there was probably a run-down house there before that got razed to make room for the new one.
The wife was there to let me in, she said now that I was there, the problem was not recurring anymore. She let me into the garage to inspect the panels. There were two panels right next to each other. The breakers were all on, but the ones they had been having trouble with were marked with masking tape. There were five of them, all double-pole 20s, with the panel label describing two circuits for each (MWBCs). There were at least 10 similar MWBCs in the two panels, and these five had been the ones giving them trouble. I looked at the circuit descriptions, and didn't see anything in particular that these 5 had in common. (But I took pictures, so I can re-look again if need be.) With the panel cover off I could verify the type of breaker, Homeline CAFCI, mainly double-pole 20s. A few other dedicated circuits were standard breakers, not AFCI. One other thing - each panel had a whole-house surge protector, and it was clear that they had been added later as an afterthought, but the homeowner said they had not added them, they were already there when they bought the house.
I verified all the connections were tight. Both panels were wired as a main panel with shared neutral/ground, and there was a 6 AWG ground wire connecting the two. Each panel had a 150A main breaker. Voltage 244: 121.1 on one leg and 122.9 on the other, checked in both panels. I looked outdoors, they had a 400A meter can with bypass lever, it was not sealed and therefore I was able to inspect all the terminations inside it as well, everything looked good, no problems. I had her start up one of the furnace blowers while I read the voltage. Voltage went from 121.1 to 121.8 on the leg I was measuring, but I couldn't be sure it was related to the furnace coming on. I explained I was looking for symptoms of a loose neutral, and not really finding them, and she said they hadn't noticed any lights dimming/brightening, so everything seemed OK there.
She said she had a science background, so I explained the theory of AFCIs, how they work and what they're supposed to do. And, I concluded that because there were multiple breakers tripping, not a specific problem with just one circuit, that whatever arc or radio-frequency noise was causing these to trip was originating outside of the house, and she should call the power company and see if they could find any problem. As I mentioned, it is an older neighborhood. The service was underground, but the power distribution lines are all overhead in the overgrown fence lines between rows of houses, and I know there is a lot of infrastructure there that is 50 to 70 years old.
I put all the covers back in place and charged a service-call fee. As I drove out of the neighborhood, I noticed there is a TV station there, only 2 blocks from the house. Not their main broadcasting tower, but a smaller tower with a doppler radar on it and a microwave link to their main tower. Could that cause noise that the AFCI breakers would pick up and misinterpret as an arc? I think it's more likely there actually was an arc on the power company lines. The homeowner said they had a similar problem about 6 months ago, but it went away and didn't happen again until last night.
AFCI troubleshooting
Probably for all you service and punch list folks. Trying to find some thoughts and tactics to find root cause of problems with an arc fault circuit without having to open a bunch of back stabbed devices, fans, lights etc. This is of course when it's already verified that it's not the breaker.
forums.mikeholt.com
A story about dual function breakers, flickering lights, and galvanic corrosion
Hi Folks, Long time lurker, first time poster. I wanted to share my story for posterity here since this forum has helped me so much in the past. If this violates the rules in any way please feel free to delete, but I hope someone might find it useful so I'll give it a go. I'm the owner of a...
forums.mikeholt.com
The call came in this morning, husband and wife wanted someone out there right away to check 3 or 4 breakers that repeatedly kept tripping. On the phone he said, "It's weird."
I pulled up to a newer house, 2 or 3 years old, of the style popular nowadays here in the south-middle-west, white with natural wood trim. The house is newer, but the neighborhood is older, and there was probably a run-down house there before that got razed to make room for the new one.
The wife was there to let me in, she said now that I was there, the problem was not recurring anymore. She let me into the garage to inspect the panels. There were two panels right next to each other. The breakers were all on, but the ones they had been having trouble with were marked with masking tape. There were five of them, all double-pole 20s, with the panel label describing two circuits for each (MWBCs). There were at least 10 similar MWBCs in the two panels, and these five had been the ones giving them trouble. I looked at the circuit descriptions, and didn't see anything in particular that these 5 had in common. (But I took pictures, so I can re-look again if need be.) With the panel cover off I could verify the type of breaker, Homeline CAFCI, mainly double-pole 20s. A few other dedicated circuits were standard breakers, not AFCI. One other thing - each panel had a whole-house surge protector, and it was clear that they had been added later as an afterthought, but the homeowner said they had not added them, they were already there when they bought the house.
I verified all the connections were tight. Both panels were wired as a main panel with shared neutral/ground, and there was a 6 AWG ground wire connecting the two. Each panel had a 150A main breaker. Voltage 244: 121.1 on one leg and 122.9 on the other, checked in both panels. I looked outdoors, they had a 400A meter can with bypass lever, it was not sealed and therefore I was able to inspect all the terminations inside it as well, everything looked good, no problems. I had her start up one of the furnace blowers while I read the voltage. Voltage went from 121.1 to 121.8 on the leg I was measuring, but I couldn't be sure it was related to the furnace coming on. I explained I was looking for symptoms of a loose neutral, and not really finding them, and she said they hadn't noticed any lights dimming/brightening, so everything seemed OK there.
She said she had a science background, so I explained the theory of AFCIs, how they work and what they're supposed to do. And, I concluded that because there were multiple breakers tripping, not a specific problem with just one circuit, that whatever arc or radio-frequency noise was causing these to trip was originating outside of the house, and she should call the power company and see if they could find any problem. As I mentioned, it is an older neighborhood. The service was underground, but the power distribution lines are all overhead in the overgrown fence lines between rows of houses, and I know there is a lot of infrastructure there that is 50 to 70 years old.
I put all the covers back in place and charged a service-call fee. As I drove out of the neighborhood, I noticed there is a TV station there, only 2 blocks from the house. Not their main broadcasting tower, but a smaller tower with a doppler radar on it and a microwave link to their main tower. Could that cause noise that the AFCI breakers would pick up and misinterpret as an arc? I think it's more likely there actually was an arc on the power company lines. The homeowner said they had a similar problem about 6 months ago, but it went away and didn't happen again until last night.