AFCI vs GFCI

Status
Not open for further replies.

WB82

Member
Location
Pennsylvania/GOM
Can an AFCI/RCCB breaker be used in place of a GFCI breaker, say for example near a sink?? A fellow co worker stated there wasn't a need to order GFCI receptacles/breakers because we already had AFCI or RCCB (merlin Gerin) breakers in our load centers. Looked into thru Schneider electrics website, but can't get a good answer. Thanks to all replys.
 

480sparky

Senior Member
Location
Iowegia
Short answer: No.

While most AFCI breakers have some degree of GFCI protection built into them, they're not approved for personnel protection.
 

gndrod

Senior Member
Location
Ca and Wa
gfci to afci

gfci to afci

Anticipating the release of the AFCI receptacle...would a GFCI breaker circuit continued into another location such as a bedroom be required to have an AFCI extended outlet?
 