dSilanskas said:Didn't for me. We had a hehumidifier in a basement on a dedicated 20 amp circuit. Well it was not labled and ended up on a ach fault breaker and of course the receptacle was a gfci. The gfci kept on tripping out and when the gfci tripped out the ach fault would trip out. We changed over to a reg. breaker and all was fine no more tripping on the gfci. But than again perhaps that was just the ach fault I had. We all know how corky they are!
"Sill light" is what we call "window candles" here. In fact, that's generally where I need to AFCI and GFCI a circuit; for window candles. There are combination AFCI/GFCI breakers now, but I don't know if they're the "combination type" (series and parallel arc). Cutler Hammer made a lot of cool AFCI's, but very few of them are planned for manufacture as the combination type, which I'm pretty bummed about.Paul B said:Has anyone put a GFCI recept on a Arc Fault circuit? I have a situation where a sill-light is is in a bathroom window. It is on a AFCI circuit. Can I put a GFCI ahead of it?
Hi Paul,Paul B said:Has anyone put a GFCI recept on a Arc Fault circuit? I have a situation where a sill-light is is in a bathroom window. It is on a AFCI circuit. Can I put a GFCI ahead of it?
Paul
They all plug in by some means, even if they appear to be hardwired. They may not all be cord and plug connected (lacking a cord on some styles), but the connect to a receptacle just the same.gndrod said:I am not sure if the sill-light term is synonymous to 'night light' as the same...so that's the reason for my dumb question. rbj
gndrod said:Hi Paul,
Maybe I am missing something here. Why would you need a GFCI if the AFCI BC sill-light in the Bathroom is direct wired and not connected to a receptacle? rbj
haskindm said:If the "sill light" is in the bathroom, why would it need to be AFCI protected? I agree that it should work just fine, but bathrooms are not listed in 210.12(B) as an area that requires AFCI protection. If it is not in the bathroom, why does it need GFCI protection. I see no reason for a receptacle to require both types of protection....
It's one timer controlled circuit for all the window candles in the whole house. This circuit weaves its way through most every room of the house; some requiring GFCI protection and some requiring AFCI protection.haskindm said:If the "sill light" is in the bathroom, why would it need to be AFCI protected? I agree that it should work just fine, but bathrooms are not listed in 210.12(B) as an area that requires AFCI protection. If it is not in the bathroom, why does it need GFCI protection. I see no reason for a receptacle to require both types of protection....
mdshunk said:It's one timer controlled circuit for all the window candles in the whole house. This circuit weaves its way through most every room of the house; some requiring GFCI protection and some requiring AFCI protection.
A wet bar in a master bedroom is another time you need to AFCI and GFCI the same circuit.
mdshunk said:It's one timer controlled circuit for all the window candles in the whole house. This circuit weaves its way through most every room of the house.