T thomasg New member May 1, 2005 #1 Hello, I am sure this has been discussed before but i cannot locate the information in the archived newsletters. Do bedroom closets require AFCI protection at the lighting fixture outlet? thank you, thomasg
Hello, I am sure this has been discussed before but i cannot locate the information in the archived newsletters. Do bedroom closets require AFCI protection at the lighting fixture outlet? thank you, thomasg
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Hospital Master Electrician May 1, 2005 #2 Re: AFCI Technically, the closet is not a bedroom or part of a bedroom. But it's faster just to include it. Any reason you have for not including on the bedroom circuit?
Re: AFCI Technically, the closet is not a bedroom or part of a bedroom. But it's faster just to include it. Any reason you have for not including on the bedroom circuit?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor May 2, 2005 #3 Re: AFCI '99 code requires that only bedroom receptacles be AFCI protected; '02 code requires that all outlets (lights, smoke detectors, etc) be so protected. [ May 02, 2005, 11:17 AM: Message edited by: LarryFine ]