In a dorm room is it required to have the lighting circuits protected on afci along with recpt circuits,cant find the code for this
 

ceb58

Senior Member
Location
Raeford, NC
In a dorm room is it required to have the lighting circuits protected on afci along with recpt circuits,cant find the code for this
Look at 210.18 I would say that a dorm room could fit into this category but if it doesn't have permanent provisions for cooking then no its not required.
 