all circuits below are 120 vac

Are AFCI's required on a dedicated circuit for a furnace?
Are AFCI's required on a dedicated circuit for a refrigerator?
Are AFCI's required on a dedicated circuit for a dishwasher?
 
all circuits below are 120 vac

Are AFCI's required on a dedicated circuit for a furnace?
No unless the furnace is in an area where afci is required
Are AFCI's required on a dedicated circuit for a refrigerator?
Not in the 2011 NEC
Are AFCI's required on a dedicated circuit for a dishwasher?
Again No

I am basing my answers on your profile that states 2011 NEC
 
what about the 2014 NEC?

In 2014 the NEC will require afci in Kitchens as well as other areas

NEC 2014 said:
210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault
circuit-interrupter protection shall be provided as required
in 210.12(A) (B), and (C). The arc-fault circuit interrupter
shall be installed in a readily accessible location.
(A) Dwelling Units. All 120-volt, single-phase, 15- and
20-ampere branch circuits supplying outlets or devices installed
in dwelling unit kitchens, family rooms, dining
rooms, living rooms, parlors, libraries, dens, bedrooms,
sunrooms, recreation rooms, closets, hallways, laundry areas,
or similar rooms or areas shall be protected by any of
the means described in 210.12(A)(1) through (6):
 