bobbymari
Senior Member
- Location
- los angeles ca
Have an issue with afci protection. We have an existing gen lighting circuit that shares a neutral with disposal circuit. Apartment rehab/remodel. We got called on not arcfaulting the existing lighting circuit since we changed devices even though circuit wasnt touched. We rectified with a 2pole afci breaker which now provides protection for disposal. Any issues "code wise" preventing this? Cant find anything. Reinspection today. Thanks