Is it required to put AFCI protection breaker for a circuit branch circuit if you’re changing out receptacles just the devices this is in Massachusetts
Not sure about in Mass but AFCI protection is required by the NEC. Here in NJ it is not required by local amendment.
406.4(D)
(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle outlet is located in any areas specified in 210.12(A) or (B), a replacement receptacle at this outlet shall be one of the following:
(1) A listed outlet branch-circuit type arc-fault circuit-interrupter receptacle
(2) A receptacle protected by a listed outlet branch-circuit type arc-fault circuit-interrupter type receptacle
(3) A receptacle protected by a listed combination type arc- fault circuit-interrupter type circuit breaker