AFCI's and Ice Melt

Status
Not open for further replies.

tonyi

Senior Member
Re: AFCI's and Ice Melt

An AFCI is in the 50ma range - close but, not quite the same.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: AFCI's and Ice Melt

Ice melting requires a listed GFP device, although the AFCI operates as a GFP device, its not listed for that purpose, You could use a combo listed afci/gfci, the trip level is 4-6 mA and may nusiance trip.
 

hurk27

Senior Member
Re: AFCI's and Ice Melt

At our IAEI meeting this month we had a rep from Cutler Hammer Showing on AFCI's and I asked this question. He called me and told me that they do have a listing for this type of use. and the GFP in their AFCI is rated at 30 Ma.
 

tonyi

Senior Member
Re: AFCI's and Ice Melt

I just got several new CH215AFIT's today and they were marked on breaker labeling as being listed for equip GFP as well as ordinary AFCI duty.

Looks like the newest stuff rolling off the line has the labeling to reflect this possible GFP usage. Good to know - the (Cutler) AFCI's are cheaper than a 30ma GFP breaker and more readily obtainable :)
 