2-124 Log #401 NEC-P02 Final Action: Reject
(210.12(B))
__________________________________________________
Submitter: David Miklos, Miklos Electric Inc.
Recommendation: Add text to read as follows:
210.12(B) Dwelling Unit Bedrooms. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms and all 120-volt, single phase, 15- and 20-ampere outlets supplying equipment installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.
Substantiation: 2005 NEC 210.12(B) Does not require AFCI protection for electric fireplaces that are installed in bedrooms because the outlets are not located in the bedrooms. The outlets are located outside of the finished bedroom walls, accessible only after removing the fireplace. The outlets are located in unfinished areas of the dwelling unit. This “Dead Space” is not within the bedrooms. Therefore, the outlet is NOT required to be AFCI protected even though the equipment it supplies is located in the bedroom.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Reject
Panel Statement: The panel intends that the current requirement applies only to branch circuits supplying outlets in bedrooms. The use of the term “equipment” is too broad in the context of the submitter’s recommendation.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
Comment on Affirmative:
BROWN, L.: Please see NAHB’s Ballot Comment on Proposal 2-142, especially the use of dwelling unit fire data to support the expansion of AFCI protection.
KING, D.: The panel action on proposal 2-142 satisfies the submitter’s intent.