mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Siemens finally admitted that standard circuit breakers and GFCIs provide combination arc fault protection. In other words the intent 210.12 could have been fulfilled with a GFCI or GFP circuit breaker.
View attachment 2555251
How are you getting that? Aren’t combination AFCIs still required to trip on series arcing faults which is the one thing breakers can’t do? If properly sized agreed breakers can trip on parallel arcing faults. Outside of residential that’s the way we’ve always do it. A “parallel” arcing fault can be as low as 40% of short circuit.
Aren’t combination AFCIs still required to trip on series arcing faults which is the one thing breakers can’t do?
well they're 'required' , but ......they don't Paul
~RJ~
well......that's a long story Paul. The stats collected by the fire service, for one, aren't universally fundedNo disagreement there. Instead of arguing about the high false positives and negatives though how about the fact that there is no evidence for the purported screw that hits the wiring causing a fire or the fact that there is no statistical evidence they work?
Regularly see 50yr old Zinsco plug-in's in mobile-home pedestals Mag trip before sub-panel breakers, with Siemens or most anything else. The notable exception is when Sqaure-D QO breakers are in the house.RMS wise. Peak wise the magnetic pickup will clear and arc fault in 1.5 cycles which fulfills UL1699.
But how much damage is done before the AFCI responds to it? Like earlier mentioned joule heating usually goes on and finally ends with short circuit or arcing.Beware, my clients occasionally report sparks & smoke from copper wire.
Zoom in on burnt neutral wire below. That's solid #12cu, no copper-clad, or aluminum anywhere in this house.
View attachment 2555292
Standard breakers let this copper wire burn up inside the bakelite box.
When AFCI's trip on similar damage, and unskilled labor cant find it, much less get past inspection, residential Electrical Contractors and their Home Builder's Association have successfully lobbied to remove AFCI's by amendment, rather than train talent to fix existing wiring, or pull armored cable to metal boxes.
If they dared to train them they could walk, and work for themselves the way I did.
holy cow!~RJ~
I doubt they want damaged equipment, but they have to know in this case that that is potentially damaging to begin with. When that fails months or years down the road it becomes "cheap junk they make nowadays in their mind". Plus it difficult to say this coating (which maybe looks more like texture overspray than paint) is absolute reason for failure, though you can't deny it is possible either, partly because same thing does happen occasionally with no foreign material on the bus. If brand new loadcenter and brand new breaker and failure in less than maybe 3-5 years though - the chances of foreign material being the problem goes up pretty dramatically I'd think.When called out for AFCI trouble, extension cord, power strip, and appliance issues can be invisible, and pass 100v megger.
Most extension cord failures only trip reset devices while smashed under furniture or chairs. The only evidence with some festoon lighting was wire insulation separating from sockets & cord caps, exposing conductors until tension was removed.
Another common issue is painting the bus stabs during remodel and tenant turnover. Zoom in on 3rd stab down from top.
View attachment 2555296
The exploit of unskilled labor is so critical to property managers, that damaged equipment is preferred to paying market rates for the skilled trades.
So what, they removed the dead front before they painted?!?When called out for AFCI trouble, extension cord, power strip, and appliance issues can be invisible, and pass 100v megger.
Most extension cord failures only trip reset devices while smashed under furniture or chairs. The only evidence with some festoon lighting was wire insulation separating from sockets & cord caps, exposing conductors until tension was removed.
Another common issue is painting the bus stabs during remodel and tenant turnover. Zoom in on 3rd stab down from top.
View attachment 2555296
The exploit of unskilled labor is so critical to property managers, that damaged equipment is preferred to paying market rates for the skilled trades.
I thought most residential panels are typically all in ones located on the exterior in So Cal?Always find fuse box & buss painted like this, when troubleshooting. The painters are long gone by the time I get there.
All apartments in Southern California have fuse box & bus stabs loaded with paint.
Doesn't matter what city, or who manages it, laborers must believe the breakers slide on easier with some fresh paint for lubricant.![]()
So order parts from some warehouse in another state and send them after itThats right, and for multi-tenant buildings the outdoor meter centers include main disconnects, with those painted ML sub-panels in each unit.
Laborers didn't mess with meter centers in the past, but recently property managers are insisting their laborers watch me work.
Sending them on parts runs helps, but once Mgmt. finds my supplier for their equipment I rarely hear from them again.