dgrey
Member
- Location
- Plymouth, MA
A little background....I recently installed a 400 a underground service to serve an existing dwelling and a large in law addition. Two meters with mains at socket . Parrallel conductors from pole to socket. Panel in main house was left as it was already served by a 4/0 SER from a meter main ( which was surplanted by a new 2 position socket). A 4/0 SER was run to inlaw MLO panel. Which leads to issue.... Problem is all AFCI and dual function AFCI/GFCI in new panel (inlaw) trip whenever something is plugged in or lights are turned on. The circuits hold until then. I investigated all the typical things, shared neutrals etc and find nothing. I cant honestly believe i would have a miswire in every circuit in the addition. My wife says I do dumb things but that would be a stretch even for me. In the meter socket the parrallel neutrals, SER neutrals, SER grounds and Earth ground all end up on the same buss at different points within the socket. I pulled all those off and had no continuity on in law SER Grd & Neut but did have continuity on older existing SER grd & neut. Found three grounds in existing panel on neutral bar moved to ground bar but that didnt change anything. Tried pulling grounds off buss in socket and just connecting them to earth ground and still nothing. I come to you, hat in hand, hoping that someone can point me in the right direction.