jxofaltrds
Inspector Mike®
- Location
- Mike P. Columbus Ohio
- Occupation
- ESI, PI, RBO
Does this exception allow me to not install an AFCI receptacle if I feed no other outlets?
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel
armored Type AC cables meeting the requirements of
250.118 and metal outlet and junction boxes are installed
for the portion of the branch circuit between the branch-circuit
overcurrent device and the first outlet, it shall be
permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining portion
of the branch circuit.
Sounds like this circuit is safe to the first outlet. So couldn't I install a single or maybe a duplex at that first outlet?
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel
armored Type AC cables meeting the requirements of
250.118 and metal outlet and junction boxes are installed
for the portion of the branch circuit between the branch-circuit
overcurrent device and the first outlet, it shall be
permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining portion
of the branch circuit.
Sounds like this circuit is safe to the first outlet. So couldn't I install a single or maybe a duplex at that first outlet?