If the only proper way to test a GFCI or an AFCI device is to push the button, then the little testers with the 3 lights and a push button are not valid testers. Correct?
Thanks
I believe it is the same for afci
I looked in the UL book 2012 but could not find the listed way of testing GFCI. I know it is listed with the instructions, but it just states "push the test button for testing" It doesn't mention that is the listed/only way of testing.
The test button on the device being the only test method recognized by the instructions is all that is the same. The way the test is performed is not the same.
Testing a GFCI with a simulated fault condition is easy to do and understand, even if it is not the recommended method, you will get consistent results.
The conditions that an AFCI are looking for are much more complex. Pressing the test button on the device likely doesn't even perform a simulation of a fault condition like the test button on the GFCI does.
Well yeah but most manufacturers have gfci built into their afci. GE is the only brand that I know about that does not have gfci built in.First off, AFCI's are AFCI's, GFCI's are GFCI's, and never the twain shall meet.
Well yeah but most manufacturers have gfci built into their afci..
The one I saw had an internal 15.87K resistor for the test load and so you get 7.6 mA and so it should trip in less than 4 seconds according to UL 943.a (presumably 6 mA) load
Well yeah but most manufacturers have gfci built into their afci. GE is the only brand that I know about that does not have gfci built in.
We all know how a GFCI operates, and the plug-in testers are a perfectly valid way of testing them. That's why UL calls them 'testers.' If theGFCI fails to trip with the tester, there is a reason - and it's either in the household wiring or the GFCI.
It it not 4-6 mA class A GFCI. A plug in GFCI tester will not trip it either.Well yeah but most manufacturers have gfci built into their afci. GE is the only brand that I know about that does not have gfci built in.
Any low impedance volt meter should draw enough. Comes in real handy for testing anything GFCI protected that is not 15 and 20 amp 125 volt receptacles.I test downstream devices with my Wiggy.
GFCI, 4-6 mA, or GFPE, 30-50 mA?
If the only proper way to test a GFCI or an AFCI device is to push the button, then the little testers with the 3 lights and a push button are not valid testers. Correct?
Thanks
AFCI indicators
Recently, there have been a number of questions from the field about the response of arc fault circuit interrupter (AFCI) circuit breakers to commercially available AFCI indicators. AFCI indicators operate by producing a waveform similar to an arc fault. However, because they cannot produce an actual arc fault, an AFCI indicator may not trip every available AFCI.
Therefore, if an AFCI indicator plugged into a receptacle protected by an AFCI does not trip the AFCI, it does not mean that the AFCI protecting the circuit is defective and needs to be replaced. When this situation occurs, you should push the "Test" button provided as an integral part of the AFCI itself. If the integral test button does not trip the AFCI circuit breaker, it should be replaced.
To notify users of this product limitation, Underwriters Laboratories Inc. requires AFCI indicators to be marked or be provided with instruction manuals that state the following or equivalent:
CAUTION: AFCIs recognize characteristics unique to arcing, and AFCI indicators produce characteristics that mimic some forms of arcing. Because of this the indicator may give a false indication that the AFCI is not functioning properly. If this occurs, recheck the operation of the AFCI using the test and reset buttons. The AFCI button test function will demonstrate proper operation.
For more information on AFCI indicators, contact Steve Brown in Melville, N.Y., by phone at +1-631-271-6200, ext. 22420; or by e-mail at Steven.A.Brown@us.ul.com. If you find a defective AFCI, please alert the product's manufacturer and UL through UL's AHJ Product Report Form available online at https://www.ul.com/regulators/ahjprod.cfm.
For more information on AFCI?s, see the AFCI section of the Regulators Page on
Correct, as UL has stated these devices are only to provide an "indication" if the receptacle or circuit is protected by an AFCI/GFCI they are not UL listed as a tester, UL only reconizes the test button on the breaker or device (GFCI receptacle) as the only listed method for testing the funtion of the AFCI/GFCI.
Here is the PDF on UL responce for AFCI's, I havent found the one for GFCI's, but I have read it.
UL about Indicators