First let me ask, please do not, I say again DO NOT, postany suggested solutions to resolve or address the scenario I am about todescribe. All I want now is your opinionas to whether this scenario would create "a problem that is in need of asolution." I will deal with possible solutions in a separate thread.
The Setup: A newbuilding will have a small generator and emergency distribution system thatmeets all the requirements in Article 700. The only loads connected to this system will be egress lights. Under this load, the emergency generator’sfuel tank will have capacity to run the generator for the minimum requirementof 90 minutes.
There will be a second generator and distribution systemdesigned under Article 702 (optional standby). The loads connected to thissystem will enable a certain number of employees to continue working. These employees would work in shifts aroundthe clock, performing services to assist other people in an off-site location,during the time that that off-site location experiences an emergencysituation. Take for granted that theemployees in this building need to be working, and that the off-site emergencycould last for several days. The optionalstandby generator’s fuel tank will have capacity to run for 48 hours at fullload, and there will be arrangements for a fuel truck to visit the facility asoften as is needed.
The Scenario: Startwith the occurrence of the off-site emergency. Suppose we are 8 hours into the emergency situation when, as nighttimehas just arrived, the utility company has a transformer failure that knocks outpower to the building. Within the next90 minutes, all non-essential people will have left the building. The people dealing with the off-site emergencykeep working. At the end of 90 minutes,the emergency generator stops, due to lack of fuel. However, if the optional standby generatorfails for any reason, the people remaining in the building will be directed togo to a backup facility to continue dealing with the off-site emergency. However, they will not have any egresslighting to lead them to the exits.
The Question: I thinkwe will all agree that this would not be a healthy situation. But is it a code violation? The code requires us to provide 90 minutes ofegress lighting. We did that. But what happens if the people choose not toegress? Fundamentally, is there aproblem that is in need of a solution?
The Setup: A newbuilding will have a small generator and emergency distribution system thatmeets all the requirements in Article 700. The only loads connected to this system will be egress lights. Under this load, the emergency generator’sfuel tank will have capacity to run the generator for the minimum requirementof 90 minutes.
There will be a second generator and distribution systemdesigned under Article 702 (optional standby). The loads connected to thissystem will enable a certain number of employees to continue working. These employees would work in shifts aroundthe clock, performing services to assist other people in an off-site location,during the time that that off-site location experiences an emergencysituation. Take for granted that theemployees in this building need to be working, and that the off-site emergencycould last for several days. The optionalstandby generator’s fuel tank will have capacity to run for 48 hours at fullload, and there will be arrangements for a fuel truck to visit the facility asoften as is needed.
The Scenario: Startwith the occurrence of the off-site emergency. Suppose we are 8 hours into the emergency situation when, as nighttimehas just arrived, the utility company has a transformer failure that knocks outpower to the building. Within the next90 minutes, all non-essential people will have left the building. The people dealing with the off-site emergencykeep working. At the end of 90 minutes,the emergency generator stops, due to lack of fuel. However, if the optional standby generatorfails for any reason, the people remaining in the building will be directed togo to a backup facility to continue dealing with the off-site emergency. However, they will not have any egresslighting to lead them to the exits.
The Question: I thinkwe will all agree that this would not be a healthy situation. But is it a code violation? The code requires us to provide 90 minutes ofegress lighting. We did that. But what happens if the people choose not toegress? Fundamentally, is there aproblem that is in need of a solution?