Natural ventilation building size limits on page B1 of AGA XFO-277 and in paragraph 6.3.2.4.5 of API-500 are mismatched.
AGA recommends that natural ventilation can be used for "...building up to 2000 square feet..."; whereas, API recommends "...1,000 cubic feet or less."
For a building that has 10' tall walls, the API limit is a 100 square foot building - twenty times more restrictive than the AGA limit!
What am I missing?