housemoney
- Midwest
- Mech Engr
Currently using the EGC as the GEC permitted by 250.121 exception without a separate GEC. Inspector is requesting a "local GEC" (circled in red below) to "ensure transformer voltage stability to ground and maintain a redundant effective ground fault current path in the event the EGC/GEC is disconnected upstream". He cited Soares: "the dual purpose conductor would have to be continuous from the equipment to the grounding electrode (red flagging terminations on equipment grounding bars in the upstream panels that feed the transformers). Ironically, the client's engineer says we don't need it as long as I'm using grounding bushings on the RMC all the way back to the service.
What's the consensus here? Is a separate GEC (circled in red below) necessary or going to do anything for these SDS's (75kVA step down transformers 480:120/208V)? All the potential grounding electrodes in the vicinity of the transformers (building steel or cable tray which is bonded to building steel) are tied together in the grounding electrode system back at the service equipment, some 300-400 feet way from the transformers.