Looking for Clarification using the NEC 2023 code. The AHJ said the cat6 Plenum cables (2) cables in 3/4 PVC in concrete to floor box under conference room table are now considered to be in a wet location because we are on the ground floor, and that we would need to either pipe all the way to the IT closet with EMT and install a outdoor/wet rated cable like OSP Cat6A so the plenum air space will not be an issue or install a J-Box and essentially do a splice , plenum to OSP.
I know that in the 2011 code we followed this rule, in Article 800.47 Underground Communications Wires and Cables Entering Buildings. The requirements that insulated conductors and cables in wet locations be listed for wet locations 310.10(C) do not apply to communications cables. https://www.mikeholt.com/instructor2/img/product/pdf/11LE-968-sample.pdf
Where is the reference in the 2023 code that would allow the exemption for communication circuits to be installed.
I know that in the 2011 code we followed this rule, in Article 800.47 Underground Communications Wires and Cables Entering Buildings. The requirements that insulated conductors and cables in wet locations be listed for wet locations 310.10(C) do not apply to communications cables. https://www.mikeholt.com/instructor2/img/product/pdf/11LE-968-sample.pdf