Quick question about AIC
I am looking at a commercial project where the plans call for a 22k AIC rated panel.
I've verified with the utility that the actual rating of the AIC at the building is 18k. This project will have a sub-panel, if the main breaker at the service is rated at
22k wouldn't I be able to use 10k rated breakers downstream at the sub-panel provided the main breaker is series rated.
This is 120/240v single phase, the main breaker will be 200amps
Thanks
I am looking at a commercial project where the plans call for a 22k AIC rated panel.
I've verified with the utility that the actual rating of the AIC at the building is 18k. This project will have a sub-panel, if the main breaker at the service is rated at
22k wouldn't I be able to use 10k rated breakers downstream at the sub-panel provided the main breaker is series rated.
This is 120/240v single phase, the main breaker will be 200amps
Thanks