Aic and short circuit ratings

Status
Not open for further replies.
I am kind of confused on which number to use from the poco to determine the aic rating for the ocp and the panel board of a service we are about to install. The poco has two options to choose from. One is the "ultimate fault current" and the other is "short circuit current". If I am using Mike Holts fault calculator which number would I enter in the utility available fault current box.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
They provide two different values because they serve two different purposes.

Most every utility i deal with says to use the 'ultimate' fault current for selecting equipment, and the available current as one possible value when determining arc flash incident energy.
 