Hello,
I'm in the process of building my retirement home. I plan on doing my own electrical with the occasional help of a retired electrician.
The pad-mounted transformer(not shared) and the meter base(Eaton CG1212P400BS) I would like to be about 12 feet away from each other. Currently, I would like to install the service with about 20' of service conductor. The extra 8' is from the length of the wire coming up out of a 3-4' deep trench.
This is what the PGE field engineer said:
Your AIC is 11,210A with the following conditions:
50 kva transformer
4/0 TX service conductor
Service run 10’
If we had to upgrade the transformer to a 75 kva your AIC would be 15,363.
So then I asked what the calculation would be at 20' and she replied: "At 20’ your AIC would be 15,599." Shouldn't this number be going down, not up with more separation? Long story short I asked her to recalculate the number for errors and she replied:" We don't have to provide AIC calculations for residential services. The customer is responsible for furnishing equipment that will withstand a maximum 22,000-amp fault current."
Unfortunately, she is new to the job and has little experience or good customer service.
My question is do you have any concerns with these numbers and can I use regular residential electrical hardware with these AIC numbers?
Thanks in advance,
Steve
I'm in the process of building my retirement home. I plan on doing my own electrical with the occasional help of a retired electrician.
The pad-mounted transformer(not shared) and the meter base(Eaton CG1212P400BS) I would like to be about 12 feet away from each other. Currently, I would like to install the service with about 20' of service conductor. The extra 8' is from the length of the wire coming up out of a 3-4' deep trench.
This is what the PGE field engineer said:
Your AIC is 11,210A with the following conditions:
50 kva transformer
4/0 TX service conductor
Service run 10’
If we had to upgrade the transformer to a 75 kva your AIC would be 15,363.
So then I asked what the calculation would be at 20' and she replied: "At 20’ your AIC would be 15,599." Shouldn't this number be going down, not up with more separation? Long story short I asked her to recalculate the number for errors and she replied:" We don't have to provide AIC calculations for residential services. The customer is responsible for furnishing equipment that will withstand a maximum 22,000-amp fault current."
Unfortunately, she is new to the job and has little experience or good customer service.
My question is do you have any concerns with these numbers and can I use regular residential electrical hardware with these AIC numbers?
Thanks in advance,
Steve