I just started using my PE and I have two questions, one regarding feeders and the second regarding AIC Calculations. I have been given a set of drawings and an existing feeder, 3 phase conductors size 2 awg are to be reused. The feeders are going to feed a Computer Room Air Conditioning unit. There will be a fused disconnect prior to the CRAC. I have 2 questions, they are as follows:
1. The CRAC will only draw approximately 70 amps. Since the existing conductors are #2 awg I assume that these feeders are protected by a circuit breaker which is much greater than 70 amps. At first I thought that maybe we would need to downsize the circuit breaker but since we are going to supply a fused disconnect at the CRAC (sized for the equipment based on manufacturers specs) then the existing breaker should be OK. Is this correct?
2. In order to determine the AIC rating of the fuses in the fused disconnect I will need to know the following:
a. AIC rating of the circuit breakers on the line side of the CRAC, meaning the feeder breaker and the main breaker in the distribution panel.
b. Impedance of the transformer feeding the distribution panel.
c. KVA Rating of the transformer feeding the distribution panel.
d. Secondary voltage of the transformer feeding the distribution panel.
e. Approximate conductor length feeding the CRAC.
Any help would be appreciated.
Thanks
1. The CRAC will only draw approximately 70 amps. Since the existing conductors are #2 awg I assume that these feeders are protected by a circuit breaker which is much greater than 70 amps. At first I thought that maybe we would need to downsize the circuit breaker but since we are going to supply a fused disconnect at the CRAC (sized for the equipment based on manufacturers specs) then the existing breaker should be OK. Is this correct?
2. In order to determine the AIC rating of the fuses in the fused disconnect I will need to know the following:
a. AIC rating of the circuit breakers on the line side of the CRAC, meaning the feeder breaker and the main breaker in the distribution panel.
b. Impedance of the transformer feeding the distribution panel.
c. KVA Rating of the transformer feeding the distribution panel.
d. Secondary voltage of the transformer feeding the distribution panel.
e. Approximate conductor length feeding the CRAC.
Any help would be appreciated.
Thanks