southernviewenergy
Member
- Location
- Cornelia, GA, United States
I am trying to figure out when a series rated AIC value is allowed for breakers in a panelboard. My situation is a 480V 1000KVA transformer that has been set for an electrical service. I have a 400A Fused Disconnect installed 15' from the transformer and a 400A Main Lug Panelboard installed 30' from the Disconnect. Inside the panelboard are (10) 30A 3 pole breakers. I know how to calculate the available fault current at a given location with the given impedance of the transformer. However, my question is, when are you allowed to series rate the breakers downstream from the Main Fused Disconnect? The Main fused disconnect has (3) 400 amp fuses that have an AIC rating of 200,000 amps. The panelboard which I ordered comes standard with 18 KAIC breakers. Do I need to specifically calculate the available fault current at each breaker or am I allowed to series rate the breakers down since I have a fuse of 200 KAIC upstream from them.
Thanks
Scott
Thanks
Scott