Hi,
I am trying to wrap my head around AIC rating.
If i have a utility transformer with an AIC of 55K and install a encloded circuit breaker that is 65k what would a subpanel have to be 150' away? Is it protecrted from the upstream device?
The proper terms are:
Amps Interrupting Capacity (AIC)- a term that applies only to protective devices that interrupt current. The value comes from the manufacturer via testing.
Short Circuit Amps (SCA)- the amount of current that will flow as the result of a short circuit fault (some times called Short Circuit, Available). the value comes from field calculations or measurements.
Short Circuit Current Rating (SCCR) - a term that applies to equipment that does not interrupter a fault, like panels, conductors, drives, and transfer switches
So,
You have a transformer/source that can produce a SCA of 55K.
You need to determine how much the impedance of your 150' of conductor will reduce this current. You also need to see if there are other sources of fault current, like motors.
Then you compare resultant SCA to the AIC or SCCR of your equipment, to see if they are at least as large as the computed SCA where it is installed. Some people like to see a 10% safety margin.
For the vast majority of situations (maybe 99.99% of the time), you should not consider that an upstream device does anything to limit the amount of fault current to downstream protective devices.
Unless you have had special training or are working under UL508A standards, the series-combination of protective devices should only be done by actual manufacturer testing.