On a 800 amp switch gear 277 480 3 phase , I need to add a 150 amp feeder breaker do I need to match the AIC rating of my 800 amp main breaker thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
On a 800 amp switch gear 277 480 3 phase , I need to add a 150 amp feeder breaker do I need to match the AIC rating of my 800 amp main breaker ghanks

The short answer is "No".

It can be higher in all cases.

It can be lower depending on the actual circumstances you have.

If the available short circuit current is less than the AIC rating of the 150A CB you can use it, even if the AIC rating is less than that of the 800 A CB.

If the 150A CB has a series rating with the 800A CB you might be able to take advantage of that.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The short answer is "No".

It can be higher in all cases.

It can be lower depending on the actual circumstances you have.

If the available short circuit current is less than the AIC rating of the 150A CB you can use it, even if the AIC rating is less than that of the 800 A CB.

If the 150A CB has a series rating with the 800A CB you might be able to take advantage of that.
Bob is correct on all counts, but I have to admit, the initial "No" got my hackles up for a moment!

The circumstances he mentions require investigation and information that may not be available to you or easy to get, so a simpler course would be to just match that rating of the main. But the issue is very valid, especially for mains, because often times larger frame breakers come with minimum AIC ratings that are higher than you need. So as long as the feeders below it are rated for the AFC (Available Fault Current), it's fine.

If there are other feeders in the panel, one way to quickly tell if the AFC is low enough or if there is a possibility of a series rating, is to look at the ratings of those other feeders. The risk however is that you are trusting the skill and judgement of the person who put n those in, and if they made a mistake, you are just continuing it. It's better to investigate it yourself.
 

topgone

Senior Member
On a 800 amp switch gear 277 480 3 phase , I need to add a 150 amp feeder breaker do I need to match the AIC rating of my 800 amp main breaker thanks

My old mentor used to tell us to match the AIC rating of the main or simply ensure that any breaker connected to the same bus should have the same AIC. When I was new to the trade, I never questioned those. :D
 