Calculated fault current at RTU (roof top unit) is 15,025A. RTU's controller data sheet shows AIC rating is 10,000A.
The RTU is protected by a fused disconnect at the unit, fuse's AIC rating is 200KA. Will this code comply even the unit's
controller AIC rating is less than calculated fault current?