mtskawasaki620
Member
- Location
- Denver, Colorado, Denver
I recently changed companies and I now quote Square D switchgear. I have been confused when building panel boards that their program doesn't allow for feed thru lugs when the AIC is higher than 22,000 on a main lug panel at 120/208V 3PH4W. In the past when quoting both Siemens and Cutler Hammer I do not remember their program not allowing for feed thru lugs above 22,000 AIC. This doesn't make sense to me as lugs do not have an over current protection so why would AIC ratings make a difference to lugs? The same could be said about lugs from Burndy, Ilsco, Penn Union, T&B.....however I have never seen an AIC rating for mechanical lugs. Below id the definition of AIC rating.
The AIC rating indicates the maximum fault current (in amps) that an overcurrent protection device (circuit breaker, fuse, etc.) will safely clear when a fault is applied at the load side of the overcurrent protection device.
Could you please clarify the reasoning behind not allowing for feed thru lugs when the AIC is above 22,000?
The AIC rating indicates the maximum fault current (in amps) that an overcurrent protection device (circuit breaker, fuse, etc.) will safely clear when a fault is applied at the load side of the overcurrent protection device.
Could you please clarify the reasoning behind not allowing for feed thru lugs when the AIC is above 22,000?