micase said:Some manufacturers show AIC ratings for relays in lighting control panels. What is the relavance of an AIC rating for a relay? Is bigger necessarily always better?
If this number is in the Ka ranges, it's a fault-current rating. Yes, bigger is better; what's required is that the rating meets or exceeds the available fault current at the terminals.jim dungar said:Are they really calling it AIC?
Amps Interrupting Capacity (AIC) is usually associated with devices which are intended to break fault currents (i.e. circuit breakers and fuses). See 110.9
LarryFine said:If this number is in the Ka ranges, it's a fault-current rating. Yes, bigger is better; what's required is that the rating meets or exceeds the available fault current at the terminals.
However, contactors open under load all the time, and this rating would be in the under-1Ka range. What is the number, and how does it compare to the relay's contact rating?
110.9 Interrupting Rating. Equipment intended to interrupt
current at fault levels shall have an interrupting rating
sufficient for the nominal circuit voltage and the current
that is available at the line terminals of the equipment.
Equipment intended to interrupt current at other than fault
levels shall have an interrupting rating at nominal circuit voltage
sufficient for the current that must be interrupted.
110.10 Circuit Impedance and Other Characteristics.
The overcurrent protective devices, the total impedance, the
component short-circuit current ratings, and other characteristics
of the circuit to be protected shall be selected and
coordinated to permit the circuit-protective devices used to
clear a fault to do so without extensive damage to the electrical
components of the circuit. This fault shall be assumed
to be either between two or more of the circuit conductors
or between any circuit conductor and the grounding conductor
or enclosing metal raceway. Listed products applied
in accordance with their listing shall be considered to meet
the requirements of this section.
georgestolz said:... it's unlikely a fault would occur at the same instant that the control wiring breaks contacts on the relay, if you think about it.
So that would fall under the second sentence of 110.9, correct?jim dungar said:That is true George, but the relay does need to be rated to close onto a fault and wait for a protective device to interrupt it.
georgestolz said:So that would fall under the second sentence of 110.9, correct?
As long as the relay was rated as normal, say 20A @ 120V or what have you, and that's the circuit it was connected to, then all would be well, right?
Edit to add: You did catch me there, I didn't think about it that way.
...circuit-protective devices used to clear a fault to do so without extensive damage to the electrical components of the circuit.
georgestolz said:I'll buy that - but would a damaged ice cube constitute "extensive damage"?
georgestolz said:Been watching Apollo 13 again, Jim?
jim dungar said:Maybe if the relay was part of the EPO for a computer room.
Imagine a situation where the relay closes onto a miswired circuit. The relay contacts vaporize at the same time as the protective device opens. The mis-wiring is corrected and the protective device is reset, because the contacts have "disappeared" it appears the problem has been solved. Next time the relay is expected to operate it won't.
I'd bet it would from the relay's point of view. :grin:georgestolz said:I'll buy that - but would a damaged ice cube constitute "extensive damage"?