sparky486
Member
- Location
- Ennis, TX USA
The OEM for a project of mine has provided 14k aic breakers to replace 35k going into a sub panel. Sub panel main is 50k, all branch circuit breakers are 35k. No calculated aic on the prints past the 2500a facility main (30,348a). I have always been under the impression that aic is aic is aic, calculated by using wire size, load, and length from utility provided rating at the 1st xfmr. They are trying to tell me that they "derated" the panel by simply providing the 14k breakers. Everything in my head says "no way".... suggestions and/or comments?