Does anyone know where i can find a code reference stating that the aic rating of the equipment must be calculated when installing new equipment? john
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: AIC ratings

Neither the designer nor the builder calculates the aic of the equipment. That information comes from the manufacturer. What must be calculated is the aic available at the equipment.

110.9 Interrupting Rating.

Equipment intended to interrupt current at fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals of the equipment.

Equipment intended to interrupt current at other than fault levels shall have an interrupting rating at nominal circuit voltage sufficient for the current that must be interrupted.
 