The circuit breaker is tested in an enclosure. However, when testing its circuit breakers, Square D often uses a shorting bar instead of 10 inches of wire on the load side.
Beginning 10/31/2000, UL 489 requires circuit breakers rated 100A
and less to additionally be tested under ?bus bar conditions.?
However, this does not assure that the circuit breaker?s interrupting
capacity equals its interrupting rating nor even that the circuit
breaker is reusable. In this test, line and load terminals are connected
to 10" of rated conductor. For single pole circuit breakers,
these 10" leads are then connected to 4' of 1 AWG for connection to
the test station. For multi-pole circuit breakers, the 10" line side
leads are connected to the test station through 4' of 1 AWG. The
load side is shorted by 10" leads of rated conductor per pole.
These ?bus bar condition? tests still do not fully address the situation
where a fault can occur less than 4'10" from the circuit breaker.
One point to be made is that acceptable bus shot test results per
the product standard do not meet the NEC? definition for a circuit
breaker. For example, 7.1.11.6.3.1 of UL 489 states ?The inability to
relatch, reclose, or otherwise reestablish continuity ... shall be considered
acceptable for circuit breakers which are tested under bus
bar conditions?.
In practical terms, this means the circuit breaker
doesn?t have to work after a fault near the circuit breaker occurs.