I calculate short-circuit current of electrical system using a method from an older Bussman Electrical Handbook. The Short-Circuit Current calculated from this method (from my understanding) should tell me what the fault current would be on the supply side of main electrical panel.
If I have a short-circuit calculations of around 12,000A, and the panelboard SCCR is 200,000A, what AIC would you most likely use? 22,000AIC, 65,000AIC? Is there a standard rate above the calculated SCC which you would select the AIC rating of the main breaker, assuming no equipment requires an AIC above 12,000A?
I calculate short-circuit current of electrical system using a method from an older Bussman Electrical Handbook. The Short-Circuit Current calculated from this method (from my understanding) should tell me what the fault current would be on the supply side of main electrical panel.
If I have a short-circuit calculations of around 12,000A, and the panelboard SCCR is 200,000A, what AIC would you most likely use? 22,000AIC, 65,000AIC? Is there a standard rate above the calculated SCC which you would select the AIC rating of the main breaker, assuming no equipment requires an AIC above 12,000A?