dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
We had a 100hp air compressor that went boom, contractor miss phased on plant outage.

We are considering a 200hp replacement we would have to rewire.

Should I simply size by 125% compressor name plate. Like a 430.22 single motor

Or do a multi motor calc for example 125% of 200hp motor + 100% of fan motor +100% of associated electronic for control boards

Thanks in advance
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
With that large of a compressor, the manufacturer should be able to give you some guidance on the ocp. It probably has a soft start or reduced voltage starter.
I think it’s going to be a star delta. We are scrambling for availability
 

jap

Senior Member
Occupation
Electrician
With that large of a compressor, the manufacturer should be able to give you some guidance on the ocp. It probably has a soft start or reduced voltage starter.

I would think so.

I would also think that an air compressor of that size would come as a packaged unit with it's own OCPD/Disconnect already installed to hit with a feeder.

JAP>
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would think so.

I would also think that an air compressor of that size would come as a packaged unit with it's own OCPD/Disconnect already installed to hit with a feeder.

JAP>
Agree....most, if not all, of the large compressors I dealt with had a factory specified main overcurrent device...often fusible.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I would think so.

I would also think that an air compressor of that size would come as a packaged unit with it's own OCPD/Disconnect already installed to hit with a feeder.

JAP>
Yes it does hav OCPD but we will need to run new branch circuit to disconnect on wall before compressor then whip to compressor. Just scrambling to get a rough bill for install materials. Our plant has 2 compressor one is supplemental and runs about 30% of time. When we find a compressor available we will have to move very quickly. If we replace with 100hp no problem so far 200hp only one available instantly
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
We had a 100hp air compressor that went boom, contractor miss phased on plant outage.

We are considering a 200hp replacement we would have to rewire.

Should I simply size by 125% compressor name plate. Like a 430.22 single motor

Or do a multi motor calc for example 125% of 200hp motor + 100% of fan motor +100% of associated electronic for control boards

Thanks in advance
Hopefully the new one will have phase loss/reversal protection built in.
 

jap

Senior Member
Occupation
Electrician
Yes it does hav OCPD but we will need to run new branch circuit to disconnect on wall before compressor then whip to compressor. Just scrambling to get a rough bill for install materials. Our plant has 2 compressor one is supplemental and runs about 30% of time. When we find a compressor available we will have to move very quickly. If we replace with 100hp no problem so far 200hp only one available instantly

You need the particulars on whatever it is that you are getting.

Generally on a compressor of that size they are self contained and you would be hitting a single point OCPD/Disconnect.

I'd find out what that is and prepare for that.

JAP>
 

retirede

Senior Member
Location
Illinois
You need the particulars on whatever it is that you are getting.

Generally on a compressor of that size they are self contained and you would be hitting a single point OCPD/Disconnect.

I'd find out what that is and prepare for that.

JAP>

For screw compressors, it’s not uncommon for the cooling module to be separate from the compressor itself. Very useful when the application includes heat recovery.
 

jap

Senior Member
Occupation
Electrician
For screw compressors, it’s not uncommon for the cooling module to be separate from the compressor itself. Very useful when the application includes heat recovery.

Agreed, but, all the advice in the world is not going to help him if it doesn't relate to what's actually going to show up.

Which we don't know.

JAP>
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Thank you for all your replies to an open ended question with many what ifs. It looks like we may have found a direct replacement one state away fingers crossed
 