dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
During a maintenance window a contractor installed a 200hp air compressor. After we got up and running I looked over the install before commissioning and I believe the wire installed is incorrect. Can someone double check me. 3 Cables plus gnd in conduit along beams and wall no other electric.
200hp compressor unit label 293 Fla/ 480 v
My math 293x 125%=366amp 500kcm copper 380 amps @75c.
Contractor ran 4/0 DLO aka NEC RHW-2 flex.
I see that as 230 amp at 75C.
Contractor said that is special high capacity cable and is why it was selected. Am I missing something here??????
Please straighten me out