Been a minute since Ive done one like this, and I was hoping one of the many minds greater than mine here, would look over what I’ve come up with.
I have delta 3-phase with high leg at the facility.
Air compressor can be wired for 208, 230, or 460, +\- 10%.
Instructions show a minimum circuit ampacity of 53 amps at 230v, and a MOCP of 110A for an inverse time CB, which is what I’ll use.
I’ve come up with #6 phase conductors, good for 65A at 75C, and a CB of 110A.
I don’t have the machine on site, so I don’t have nameplate FLC, but I have the manufacturer’s instructions that 110A is the maximum, so even if 430.52 allowed a larger CB, I would have to stick with 110.
Since the MOCP is 110A, per 250.122, I will need to use a #6 for the EGC as well.
Did I make a mistake on this?
Just hope my supplier can get me orange #6.